Question 1104 of 731 · Texas Journeyman Electrician Exam
Unless the equipment is listed and marked otherwise, terminations for circuits rated 100 amperes or less (or 14 AWG through 1 AWG conductors) are based on which conductor temperature rating?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1104
- C: 60 degrees C
Explanation
110.14(C)(1)(a) bases termination provisions for these smaller circuits on 60 degrees C conductor ampacity unless the equipment is listed and identified for 75 degrees C. A 90 degree conductor may be used, but its ampacity is limited to the termination rating.
More questions: Definitions, Theory and Plans
- 1105For circuits rated over 100 amperes, or conductors larger than 1 AWG, terminations are generally based on which conductor temperature column?
- 1106Copper and aluminum conductors may be joined in the same terminal or splicing connector only when:
- 1108The required depth of working space in front of a 120/240-volt panelboard (150 volts or less to ground) is, for all conditions:
- 1109A 480Y/277-volt panelboard has exposed live parts on one side of the working space and a grounded concrete wall on the other (Condition 2). What is the minimum depth of working space?
- 1110Equipment at 277 volts to ground has exposed live parts on both sides of the working space (Condition 3). The minimum working space depth is: