For circuits rated over 100 amperes, or conductors larger than 1 AWG, terminations are generally based on which conductor temperature column?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1105
- D: 75 degrees C
Explanation
110.14(C)(1)(b) permits conductors for circuits over 100 A or larger than 1 AWG to be used at their 75 degree C ampacity, unless the equipment is listed for a higher temperature.