Using the standard method under the NEC 2026, what general lighting load must be included in the service calculation for a one-family dwelling with 2,400 ft2 of livable floor area?

Exactly one answer is correct.

Show solution

Correct answer to question 12001

  • A: 4,800 VA

Explanation

The dwelling unit load for general lighting and general-use receptacles is 2 VA per ft2 (120.41). 2,400 ft2 x 2 VA = 4,800 VA. Garages, open porches and unfinished spaces not adaptable for future use are not counted.