Under the NEC 2026 standard method, what is the demand load for general lighting, two small-appliance circuits and one laundry circuit in a 4,500 ft2 dwelling?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12004
- D: 6,675 VA
Explanation
4,500 ft2 x 2 VA = 9,000 VA, plus 4,500 VA for the small-appliance and laundry circuits = 13,500 VA. First 3,000 VA at 100 % and the remaining 10,500 VA at 35 % gives 6,675 VA (Table 120.45).
More questions: Load Calculations
- 12005Optional method (NEC 2026): a 2,000 ft2 dwelling has two small-appliance circuits, one laundry circuit, a 12 kW range, a 5 kW dryer, a 1,200 VA dishwasher and a 4,500 W water heater. What is the calculated general load (heating and AC excluded)?
- 12006Optional method (NEC 2026), 120/240 V service: 1,800 ft2 dwelling, two small-appliance and one laundry circuit, 11 kW range, 5.5 kW dryer, 1,000 VA dishwasher, 800 VA disposal, 4 kW water heater, 6,000 VA central AC and 8 kW central electric furnace. What is the calculated load in amperes?
- 12007Optional method (NEC 2026): a 1,500 ft2 dwelling with two small-appliance and one laundry circuit, a 10 kW range, 5 kW dryer and 4.5 kW water heater has six separately controlled 2 kW baseboard heaters and a 4,000 VA AC unit. What is the total calculated load?
- 12009Under the NEC 2026, what is the minimum number of 15 A, 120 V general lighting branch circuits for a 2,600 ft2 dwelling?
- 12010How many 20 A, 120 V general lighting branch circuits are required at minimum for a 3,400 ft2 dwelling under the NEC 2026?
- 12011Under the NEC 2026, what is the feeder demand load for four 5.5 kW household electric dryers in an apartment building?