How many 20 A, 120 V general lighting branch circuits are required at minimum for a 3,400 ft2 dwelling under the NEC 2026?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12010
- B: 5
Explanation
Circuit count uses 3 VA per ft2 (120.13): 3,400 x 3 = 10,200 VA. A 20 A, 120 V circuit supplies 2,400 VA, and 10,200 / 2,400 = 4.25, so 5 circuits are needed (always round up). Small-appliance and laundry circuits are in addition.