Question 12009 of 731 · Texas Journeyman Electrician Exam

Under the NEC 2026, what is the minimum number of 15 A, 120 V general lighting branch circuits for a 2,600 ft2 dwelling?

Exactly one answer is correct.

Show solution

Correct answer to question 12009

  • A: 5

Explanation

For counting branch circuits the dwelling unit load stays at 3 VA per ft2 (120.13): 2,600 x 3 = 7,800 VA. Each 15 A, 120 V circuit carries 1,800 VA, so 7,800 / 1,800 = 4.33, rounded up to 5 circuits. The 2 VA value of 120.41 applies only to service and feeder calculations.