Under the NEC 2026, what is the minimum number of 15 A, 120 V general lighting branch circuits for a 2,600 ft2 dwelling?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12009
- A: 5
Explanation
For counting branch circuits the dwelling unit load stays at 3 VA per ft2 (120.13): 2,600 x 3 = 7,800 VA. Each 15 A, 120 V circuit carries 1,800 VA, so 7,800 / 1,800 = 4.33, rounded up to 5 circuits. The 2 VA value of 120.41 applies only to service and feeder calculations.
More questions: Load Calculations
- 12010How many 20 A, 120 V general lighting branch circuits are required at minimum for a 3,400 ft2 dwelling under the NEC 2026?
- 12011Under the NEC 2026, what is the feeder demand load for four 5.5 kW household electric dryers in an apartment building?
- 12012Five 5 kW household dryers are supplied by one feeder. What is the calculated dryer load under the NEC 2026?
- 12013Ten 5 kW electric dryers in a multifamily building are on one service. Using the NEC 2026 dryer demand factors, what is the dryer load?
- 12014Under the NEC 2026, what is the demand factor for 15 household electric dryers on one feeder?
- 12015A dwelling has one electric dryer rated 4,400 W. What load must be used for it in the NEC 2026 service calculation?