A 120/240 volt single-phase 3-wire feeder carries 40 A on one ungrounded conductor and 25 A on the other. Assuming linear loads, what current flows in the neutral?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13018
- B: 15 A
Explanation
On a 120/240 V 3-wire system the neutral carries only the unbalanced current: 40 A minus 25 A = 15 A. Adding the currents (65 A) is the typical mistake.