Question 13053 of 731 · Texas Journeyman Electrician Exam

Three current-carrying 2 AWG THHN copper conductors are installed at 35 °C ambient and terminate on 75 °C rated lugs. What is the maximum load current the conductors may be used for?

Exactly one answer is correct.

Show solution

Correct answer to question 13053

  • A: 115 A

Explanation

The corrected 90 °C ampacity is 130 x 0.96 = 124.8 A, but the 75 °C termination limits the conductor to its 75 °C value of 115 A. The lower value, 115 A, applies.

Next to question ›