Question 13059 of 731 · Texas Journeyman Electrician Exam
A 50 A noncontinuous load is supplied by one of six current-carrying THHN copper conductors in a raceway at 30 °C. Terminations are rated 75 °C. What is the smallest conductor size permitted?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13059
- C: 6 AWG
Explanation
8 AWG derates to 55 x 0.80 = 44 A, which is below 50 A. 6 AWG derates to 75 x 0.80 = 60 A and its 75 °C rating of 65 A also covers the 50 A load, so 6 AWG is the minimum.
More questions: Electrical Calculations
- 13060Twenty current-carrying 12 AWG THHN copper conductors are in one raceway at 30 °C ambient. What is the adjusted ampacity based on the 90 °C column?
- 13061What adjustment factor applies when 25 current-carrying conductors are installed in a single raceway longer than 24 inches?
- 13062What ambient temperature correction factor applies to a 75 °C rated conductor at an ambient of 38 °C (tables based on 30 °C)?
- 13063A device box contains four 12 AWG insulated conductors, two 12 AWG equipment grounding conductors and one receptacle on a yoke. What minimum box volume is required?
- 13064A box has internal cable clamps, six 14 AWG insulated conductors, two 14 AWG equipment grounding conductors and a single-pole switch. What minimum volume does 314.16 require?
- 13065A box has a marked volume of 18.0 cubic inches and will contain only 12 AWG conductors with no fittings, devices or grounding conductors. What is the maximum number of conductors permitted?