What ambient temperature correction factor applies to a 75 °C rated conductor at an ambient of 38 °C (tables based on 30 °C)?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13062
- B: 0.88
Explanation
In the 75 °C column, the factor for 36 to 40 °C is 0.88. 0.91 is the 90 °C column value for the same range, and 0.94 belongs to 31 to 35 °C.