Question 13095 of 731 · Texas Journeyman Electrician Exam

A 1 hp, 115 volt, single-phase motor has a table full-load current of 16 A. What minimum branch-circuit conductor ampacity is required?

Exactly one answer is correct.

Show solution

Correct answer to question 13095

  • C: 20 A

Explanation

The conductors must be rated at least 125 % of the table current: 16 x 1.25 = 20 A. 8 A is the 230 V full-load current for the same motor.

Next to question ›