A balanced three-phase load draws 150 A per phase at 208 volts. What is the minimum transformer kVA required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13106
- B: 54.0 kVA
Explanation
kVA = E x I x 1.732 / 1,000 = 208 x 150 x 1.732 / 1,000 = 54.0 kVA. Omitting 1.732 gives the single-phase value of 31.2 kVA.
More questions: Electrical Calculations
- 13107A transformer delivers 48.5 kW to its load while its input is 50 kW. What is its efficiency?
- 13108A 15 kVA, single-phase transformer with a 240 volt primary is protected on the primary side only. Which statement about its primary current is correct?
- 13109A branch circuit supplies a 36 A continuous load and nothing else. What is the minimum overcurrent device rating?
- 13110A 40 A continuous load is supplied with THWN copper conductors terminating on 75 °C rated equipment. What is the minimum conductor size?
- 13111A branch circuit supplies 30 A of continuous load and 20 A of noncontinuous load. What is the minimum standard overcurrent device rating?