What is the maximum continuous load permitted on a 20 A branch circuit protected by a standard (not 100 % rated) breaker?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13112
- D: 16 A
Explanation
A continuous load may not exceed 80 % of the overcurrent device rating, which is the inverse of the 125 % rule: 20 x 0.80 = 16 A. Loading the circuit to the full 20 A is allowed only for noncontinuous loads.
More questions: Electrical Calculations
- 13113What is the maximum continuous lighting load in volt-amperes on a 277 volt, 20 A branch circuit?
- 13114How many 277 volt LED luminaires drawing 0.75 A each may be connected to a 20 A branch circuit if they operate continuously?
- 13115A three-phase feeder supplies 120 A of continuous load and 40 A of noncontinuous load. What is the minimum standard overcurrent device rating?
- 13116A 24 A continuous load is supplied by a branch circuit. What is the minimum overcurrent device rating and minimum copper conductor size with 60 °C terminations?
- 13118A single-phase 240 volt, 10 kW heater operates for 3 hours. How many kilowatt-hours does it use, and what is its current?