Question 13114 of 731 · Texas Journeyman Electrician Exam
How many 277 volt LED luminaires drawing 0.75 A each may be connected to a 20 A branch circuit if they operate continuously?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13114
- B: 21
Explanation
The continuous limit is 16 A, and 16 / 0.75 = 21.3, which rounds down to 21 luminaires. Using the full 20 A gives 26.
More questions: Electrical Calculations
- 13115A three-phase feeder supplies 120 A of continuous load and 40 A of noncontinuous load. What is the minimum standard overcurrent device rating?
- 13116A 24 A continuous load is supplied by a branch circuit. What is the minimum overcurrent device rating and minimum copper conductor size with 60 °C terminations?
- 13118A single-phase 240 volt, 10 kW heater operates for 3 hours. How many kilowatt-hours does it use, and what is its current?
- 13119What is the circular mil area of a 10 AWG conductor as listed in Chapter 9 Table 8?
- 13120A 240 volt, single-phase, 2 hp motor has a table full-load current of 12 A at 230 volts. What is the minimum branch-circuit conductor ampacity?
- 13121Three-phase 460 volt motors are rated 5 hp (7.6 A) and 3 hp (4.8 A). What is the minimum ampacity of a feeder supplying only these two motors?