A 120/240 volt service drop passes over a roof with a slope of 4 in 12. What is the minimum clearance above the roof permitted by the exception for sloped roofs?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2004
- C: 3 ft
Explanation
Where the voltage between conductors is 300 volts or less and the roof has a slope of 4 in 12 or greater, the clearance may be reduced to 3 ft. See 230.24(A) Exception No. 2.