Overhead service conductors run beside a window that is designed to be opened. What minimum horizontal clearance from the window is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2006
- B: 3 ft
Explanation
Service conductors must be kept at least 3 ft from windows designed to be opened, doors, porches, balconies, ladders, stairs and fire escapes. Conductors run above the top level of a window are exempt. See 230.9(A).