Question 2016 of 731 · Texas Journeyman Electrician Exam
Where must a service head generally be located in relation to the point of attachment of the service drop?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2016
- D: Above the point of attachment
Explanation
Service heads must be above the point of attachment so that water does not run into the raceway. Where that is impracticable, they may be within 24 in. of the point of attachment. Drip loops are formed below the service head. See 230.54(C).
More questions: Services and Service Equipment
- 2017What is the minimum width of the working space in front of service equipment?
- 2018Which of the following may not be used to support overhead conductor spans?
- 2019Which types of surge protective device satisfy the dwelling unit service surge protection rule?
- 2020Service-entrance cable run on the outside of a building must be supported within 12 in. of the service head and at intervals not exceeding what distance?
- 2021A commercial service supplies 120 A of continuous load and 40 A of noncontinuous load. What is the minimum ampacity of the service-entrance conductors?
- 2022Under the 2020 and later editions, how must two to six service disconnects for one service be arranged?