A commercial service supplies 120 A of continuous load and 40 A of noncontinuous load. What is the minimum ampacity of the service-entrance conductors?

Exactly one answer is correct.

Show solution

Correct answer to question 2021

  • C: 190 A

Explanation

Service-entrance conductors must carry 125 percent of the continuous load plus 100 percent of the noncontinuous load. 120 A times 1.25 is 150 A, plus 40 A gives 190 A. See 230.42(A).