Service-entrance cable run on the outside of a building must be supported within 12 in. of the service head and at intervals not exceeding what distance?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2020
- C: 30 in.
Explanation
Service cables must be secured within 12 in. of every service head, gooseneck or connection to a raceway or enclosure, and at intervals not exceeding 30 in. See 230.51(A).