An overhead outside branch circuit spans 60 ft between supports. What is the minimum copper conductor size?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2027
- C: 8 AWG
Explanation
For overhead spans of 1000 volts or less, copper must be at least 10 AWG for spans up to 50 ft and 8 AWG for longer spans, unless supported by a messenger. See 225.6(A).