Service drop conductors at 120/240 volts pass over only the overhang of a roof to terminate at a through-the-roof service mast. What is the minimum clearance above the overhang?

Exactly one answer is correct.

Show solution

Correct answer to question 2034

  • D: 18 in.

Explanation

The overhang exception allows 18 in. where not more than 6 ft of conductors, 4 ft horizontally, pass over the roof overhang and terminate at a through-the-roof raceway or approved support. The voltage between conductors must not exceed 300 volts. See 230.24(A) Exception No. 3.