Question 2041 of 731 · Texas Journeyman Electrician Exam

A detached building is supplied by one feeder. Where must its building disconnecting means be located?

Exactly one answer is correct.

Show solution

Correct answer to question 2041

  • A: Outside, or inside nearest the point of entrance of the feeder conductors

Explanation

A building supplied by a feeder needs its own disconnect, readily accessible and located outside or inside nearest the point of entrance of the conductors. See 225.31 and 225.32.

Next to question ›