Where may the service disconnecting means for a commercial building be installed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2042
- C: At a readily accessible location outside, or inside nearest the point of entrance of the service conductors
Explanation
The service disconnect must be readily accessible, either outside the building or inside nearest the point where the service conductors enter. This keeps unprotected service conductors inside the building short. See 230.70(A).