Question 2047 of 731 · Texas Journeyman Electrician Exam
Which of the following is permitted to be connected on the supply side of the service disconnecting means?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2047
- D: A meter
Explanation
Only specific equipment may be installed ahead of the service disconnect, including cable limiters, meters, meter disconnect switches, instrument transformers and surge protective devices. General branch circuits are not on the list. See 230.82.
More questions: Services and Service Equipment
- 2048Which situation permits an additional service to a building?
- 2050A service drop cable with a bare messenger operates at 120/240 volts. What is the minimum clearance above a sidewalk accessible only to pedestrians?
- 2051At a supply voltage of 1000 volts or less, additional services are permitted for capacity reasons when the load exceeds what value?
- 2052A service disconnect supplies only two 2-wire branch circuits. What is its minimum rating?
- 2053What is the minimum depth of working space in front of a 120/240 volt panelboard with live parts on one side and no grounded parts on the other (Condition 1)?
- 2054Under the 2026 NEC, where must the service disconnecting means for a one-family dwelling be located?