Question 2054 of 731 · Texas Journeyman Electrician Exam
Under the 2026 NEC, where must the service disconnecting means for a one-family dwelling be located?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2054
- A: In a readily accessible outdoor location on or within sight of the dwelling
Explanation
The 2026 edition deleted 230.85 and moved the emergency disconnect idea into 230.70(A)(1): the service disconnect for one- and two-family dwellings goes outdoors, on or within sight of the dwelling. An exception applies where an emergency disconnect is provided per 225.41.
More questions: Services and Service Equipment
- 2055Under the 2026 NEC, what happened to section 230.85 Emergency Disconnects?
- 2056How is the overcurrent protection for each ungrounded service conductor generally sized?
- 2057What is the maximum number of disconnects permitted for a building supplied by one outside feeder?
- 2058What is the minimum height above finished grade for the point of attachment of a service drop to a building?
- 2059Ground-fault protection of equipment is required for a service disconnect rated 1200 A on which system?
- 2061Overhead feeder conductors run from a house to a detached garage at 120/240 volts. What is the minimum clearance above the residential driveway?