Question 2055 of 731 · Texas Journeyman Electrician Exam
Under the 2026 NEC, what happened to section 230.85 Emergency Disconnects?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2055
- C: It was deleted and its requirements were moved into 230.70
Explanation
The 2026 edition deleted 230.85 and incorporated the outdoor location and marking rules into 230.70(A)(1) and 230.70(B). For dwellings supplied by feeders, the emergency disconnect remains in 225.41.
More questions: Services and Service Equipment