Question 2059 of 731 · Texas Journeyman Electrician Exam
Ground-fault protection of equipment is required for a service disconnect rated 1200 A on which system?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2059
- B: 480Y/277 volt, 3-phase, 4-wire solidly grounded wye
Explanation
GFPE applies to solidly grounded wye services of more than 150 volts to ground for each disconnect rated 1000 A or more. A 480Y/277 volt system is 277 volts to ground, while 208Y/120 volt is only 120 volts to ground. See 230.95.
More questions: Services and Service Equipment
- 2061Overhead feeder conductors run from a house to a detached garage at 120/240 volts. What is the minimum clearance above the residential driveway?
- 2062May branch circuit conductors be installed in the same raceway as service-entrance conductors?
- 2002What is the maximum number of service disconnects permitted for one service?
- 2004A 120/240 volt service drop passes over a roof with a slope of 4 in 12. What is the minimum clearance above the roof permitted by the exception for sloped roofs?
- 2005Overhead service conductors cross a public street that is subject to truck traffic. What is the minimum vertical clearance above the street?
- 2006Overhead service conductors run beside a window that is designed to be opened. What minimum horizontal clearance from the window is required?