A service drop cable with a bare messenger operates at 120/240 volts. What is the minimum clearance above a sidewalk accessible only to pedestrians?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2050
- C: 10 ft
Explanation
A 10 ft clearance is permitted above finished grade, sidewalks and pedestrian-only platforms where the voltage does not exceed 150 volts to ground and the conductors are cabled together with a grounded bare messenger. A 120/240 volt system is 120 volts to ground. See 230.24(B).