A service disconnect supplies only two 2-wire branch circuits. What is its minimum rating?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2052
- D: 30 amperes
Explanation
A two-circuit installation requires a service disconnect rated at least 30 amperes. A single-circuit installation may be 15 amperes. See 230.79(B).