Question 2036 of 731 · Texas Journeyman Electrician Exam
What must be done with a service GFPE system when it is first installed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2036
- D: It must be performance tested on site, with a written record
Explanation
The GFPE system must be performance tested when first installed, by a qualified person using primary current injection per the manufacturer's instructions. A written record must be available to the AHJ. See 230.95.
More questions: Services and Service Equipment
- 2037What is the minimum height of working space for service equipment rated 1000 volts or less?
- 2038Under the 2023 and 2026 NEC, surge protection at the service is required for dwelling units and also for which of the following?
- 2039Service conductors installed under a building are considered outside the building when they are covered by at least how much concrete?
- 2040How must each service disconnect be identified?
- 2041A detached building is supplied by one feeder. Where must its building disconnecting means be located?
- 2042Where may the service disconnecting means for a commercial building be installed?