Where must the service overcurrent device be located relative to the service disconnect?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2029
- A: Part of the service disconnect or immediately adjacent to it
Explanation
The service OCPD must be an integral part of the service disconnecting means or located immediately adjacent to it. See 230.91.
More questions: Services and Service Equipment
- 2030What is the maximum ground-fault trip setting permitted for service GFPE?
- 2033What may be attached to a service mast that supports a service drop?
- 2034Service drop conductors at 120/240 volts pass over only the overhang of a roof to terminate at a through-the-roof service mast. What is the minimum clearance above the overhang?
- 2036What must be done with a service GFPE system when it is first installed?
- 2037What is the minimum height of working space for service equipment rated 1000 volts or less?
- 2038Under the 2023 and 2026 NEC, surge protection at the service is required for dwelling units and also for which of the following?