Question 2026 of 731 · Texas Journeyman Electrician Exam
What is the minimum size aluminum conductor permitted for an underground service lateral serving a general load?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2026
- A: 6 AWG
Explanation
Underground service conductors must not be smaller than 8 AWG copper or 6 AWG aluminum or copper-clad aluminum. A smaller size is allowed only for limited loads such as a single branch circuit. See 230.31(B).
More questions: Services and Service Equipment
- 2027An overhead outside branch circuit spans 60 ft between supports. What is the minimum copper conductor size?
- 2028What is the minimum vertical clearance for overhead service conductors above a residential driveway when the voltage does not exceed 300 volts to ground?
- 2029Where must the service overcurrent device be located relative to the service disconnect?
- 2030What is the maximum ground-fault trip setting permitted for service GFPE?
- 2033What may be attached to a service mast that supports a service drop?
- 2034Service drop conductors at 120/240 volts pass over only the overhang of a roof to terminate at a through-the-roof service mast. What is the minimum clearance above the overhang?