Question 2017 of 731 · Texas Journeyman Electrician Exam
What is the minimum width of the working space in front of service equipment?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2017
- C: 30 in. or the width of the equipment, whichever is greater
Explanation
The working space must be at least 30 in. wide or the width of the equipment, whichever is greater. The equipment does not need to be centered in the space. See 110.26(A)(2).
More questions: Services and Service Equipment
- 2018Which of the following may not be used to support overhead conductor spans?
- 2019Which types of surge protective device satisfy the dwelling unit service surge protection rule?
- 2020Service-entrance cable run on the outside of a building must be supported within 12 in. of the service head and at intervals not exceeding what distance?
- 2021A commercial service supplies 120 A of continuous load and 40 A of noncontinuous load. What is the minimum ampacity of the service-entrance conductors?
- 2022Under the 2020 and later editions, how must two to six service disconnects for one service be arranged?
- 2023A service supplies a small commercial building, not a dwelling, with more than two branch circuits. What is the minimum service disconnect rating?