Under the 2023 and 2026 NEC, what minimum nominal discharge current rating must a required service SPD have?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2009
- D: 10 kA
Explanation
The 2023 edition added a minimum nominal discharge current rating of 10 kA for the SPD required at dwelling services. The same rating is required for feeder SPDs under 215.18.