Question 2015 of 850 · Texas Journeyman Electrician Exam
Under the 2023 and 2026 NEC, when is surge protection required for an existing dwelling service?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2015
- B: When the service equipment is replaced
Explanation
Starting with 2023, 230.67 applies when service equipment is replaced, not only to new services. A meter change by the utility does not trigger it. See 230.67.