Question 3014 of 731 · Texas Journeyman Electrician Exam
Which of the following is not a standard ampere rating for an inverse time circuit breaker?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3014
- B: 275 A
Explanation
Standard ratings in this range are 200, 225, 250, 300 and 350 A. There is no standard 275 A rating. See 240.6(A).
More questions: Feeders and Overcurrent Protection