Under the 25 ft feeder tap rule, what minimum ampacity must the tap conductors have?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3015
- C: One-third of the feeder OCPD rating
Explanation
Taps not over 25 ft long must have an ampacity of at least one-third of the feeder OCPD rating. They must end in a single circuit breaker or single set of fuses that limits the load to the tap ampacity. See 240.21(B)(2).