Under the NEC 2023 and 2026, a 125-volt receptacle installed behind the refrigerator in a dwelling kitchen does not serve the countertop and is more than 6 ft from the sink. Is GFCI protection required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4006
- B: Yes, all receptacles in dwelling kitchens are covered
Explanation
Starting with the 2023 edition, the kitchen item in 210.8(A) applies to all receptacles in the kitchen, not only those serving the countertop. The refrigerator receptacle therefore needs GFCI protection.
More questions: Branch Circuits, GFCI and AFCI
- 4007Under the NEC 2023 and 2026, a dwelling family room has a wet bar with a sink and permanent provisions for beverage preparation. A receptacle in this bar area is 8 ft from the sink. Is GFCI protection required?
- 4009A dwelling has a fully finished basement used as a recreation room. Do the 125-volt receptacles in this finished basement require GFCI protection?
- 4010A single 125-volt receptacle in an attached dwelling garage is dedicated to a chest freezer. Is GFCI protection required?
- 4011Under the 2026 NEC, a detached dwelling storage building has a wood floor framed 2 ft above grade and is not intended as a habitable room. Do its 125-volt receptacles require GFCI protection under 210.8(A)?
- 4013Where must a GFCI device that provides the protection required by 210.8 be located?
- 4014When applying the 6 ft sink and bathtub distances in 210.8, how is the distance to a receptacle measured?