Question 4032 of 931 · Texas Journeyman Electrician Exam
Under 210.8(F), which dwelling unit outdoor outlets are generally not required to have GFCI protection?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4032
- C: Lighting outlets other than those in crawl spaces
Explanation
210.8(F) has an exception for lighting outlets, except the crawl space lighting outlets that have their own GFCI rule. Other outdoor outlets within the voltage and current limits are covered.
More questions: Branch Circuits, GFCI and AFCI