Question 4084 of 731 · Texas Journeyman Electrician Exam
On a 20-ampere branch circuit, what is the maximum rating of a single cord-and-plug-connected utilization equipment not fastened in place?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4084
- B: 16 amperes
Explanation
210.23 limits any one cord-and-plug-connected utilization equipment not fastened in place to 80 percent of the branch circuit rating on 15- and 20-ampere circuits. For a 20-ampere circuit that is 16 amperes.
More questions: Branch Circuits, GFCI and AFCI
- 4085A 20-ampere branch circuit supplies lighting units and also fastened-in-place utilization equipment. What is the maximum total rating of the fastened-in-place equipment?
- 4086Which loads are 40-ampere and 50-ampere branch circuits permitted to supply in any occupancy?
- 4087In a dwelling unit, a 30-ampere branch circuit is permitted to supply which of the following?
- 4088A branch circuit supplies a continuous load of 16 amperes and no noncontinuous load. What is the minimum conductor ampacity before any adjustment or correction?
- 4089A branch circuit supplies 24 amperes of continuous load and 6 amperes of noncontinuous load. What is the minimum standard overcurrent device rating?
- 4090For branch circuit sizing, a continuous load is one where the maximum current is expected to continue for how long?