A ground rod measured 40 ohms, so a second rod was driven 6 ft away. The pair still measures 30 ohms. What else is required?

Exactly one answer is correct.

Show solution

Correct answer to question 5013

  • A: Nothing further is required by the Code

Explanation

Once the single rod is supplemented by a properly spaced additional electrode, the Code does not require further electrodes even if 25 ohms is not reached. See 250.53.