Question 5017 of 731 · Texas Journeyman Electrician Exam
The portion of a GEC that is the sole connection to a ground ring is not required to be larger than
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5017
- A: The conductor used for the ground ring
Explanation
Where the GEC connects only to a ground ring, it need not be larger than the conductor used for the ring itself. See 250.66(C).