A service has two parallel sets of 3/0 AWG copper (about 168 kcmil each). What is the minimum copper GEC to a water pipe electrode?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5021
- A: 2 AWG
Explanation
For parallel sets, the GEC is sized on the equivalent area of the paralleled conductors: 2 x 167.8 kcmil = 335.6 kcmil. That falls in the over 3/0 through 350 kcmil row of Table 250.66, which requires 2 AWG copper.