In NEC 2026, the requirement to bond ferrous enclosures of a GEC at both ends was expressly extended to include
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5028
- D: Ferrous metal cable armor
Explanation
NEC 2026 250.64(E)(1) adds cable armor to the rule, so ferrous cable armor around a GEC must be bonded at both ends like a ferrous raceway. Unbonded ferrous armor would act as a choke and raise the impedance of the GEC path.
More questions: Grounding and Bonding
- 5030At the service, the main bonding jumper connects
- 5031What is the minimum size copper main bonding jumper for a service with 4/0 AWG copper ungrounded conductors?
- 5032A service has four parallel sets of 500 kcmil copper per phase (2000 kcmil total). What is the minimum copper main bonding jumper?
- 5033A subpanel in the same building is fed by a feeder from the service. How must the grounded (neutral) conductor be treated at the subpanel?
- 5034For a grounded service, the GEC connection to the grounded service conductor is permitted
- 5035What is the minimum copper equipment grounding conductor for a circuit protected by a 20 A OCPD?