Question 5033 of 731 · Texas Journeyman Electrician Exam
A subpanel in the same building is fed by a feeder from the service. How must the grounded (neutral) conductor be treated at the subpanel?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5033
- A: Isolated from the enclosure and the EGC bar
Explanation
A grounded conductor may not be connected to normally non-current-carrying metal parts or EGCs on the load side of the service disconnect. Bonding there would put neutral current on the EGCs. See 250.24(A)(5) and 250.142(B).
More questions: Grounding and Bonding
- 5034For a grounded service, the GEC connection to the grounded service conductor is permitted
- 5035What is the minimum copper equipment grounding conductor for a circuit protected by a 20 A OCPD?
- 5036What is the minimum copper equipment grounding conductor for a feeder protected by a 100 A OCPD?
- 5037What is the minimum copper equipment grounding conductor for a feeder protected by a 400 A OCPD?
- 5038A 20 A branch circuit is upsized from 12 AWG to 10 AWG copper to limit voltage drop. What is the minimum copper EGC?
- 5039A 60 A circuit is upsized from 6 AWG to 4 AWG copper for voltage drop. What is the minimum copper EGC?