What is the minimum copper equipment grounding conductor for a circuit protected by a 20 A OCPD?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5035
- C: 12 AWG
Explanation
Table 250.122 sizes the EGC on the rating of the OCPD ahead of the equipment. A 20 A device requires at least 12 AWG copper.