A 1200 A feeder is run in four parallel raceways, each with its own copper EGC. What is the minimum EGC in each raceway?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5040
- D: 3/0 AWG in each raceway
Explanation
Where conductors are paralleled in multiple raceways, the EGC in each raceway must be full size based on the feeder OCPD per Table 250.122. For 1200 A that is 3/0 copper in each raceway. See 250.122(F).