Question 5038 of 731 · Texas Journeyman Electrician Exam
A 20 A branch circuit is upsized from 12 AWG to 10 AWG copper to limit voltage drop. What is the minimum copper EGC?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5038
- B: 10 AWG
Explanation
When ungrounded conductors are increased in size, the EGC must be increased proportionally by circular mil area. 10,380 / 6,530 = 1.59, and 6,530 x 1.59 = 10,380 cmil, which is 10 AWG. See 250.122(B).