NEC 2026 added which method for splicing a grounding electrode conductor, in addition to irreversible compression and exothermic welding?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5026
- B: Listed grounding and bonding fittings in an accessible location
Explanation
NEC 2026 250.64(C) permits splicing the GEC with listed grounding and bonding equipment where the splice is accessible. Irreversible compression and exothermic welding remain permitted in accessible and concealed locations.
More questions: Grounding and Bonding
- 5027A ferrous metal raceway that encloses a grounding electrode conductor must be
- 5028In NEC 2026, the requirement to bond ferrous enclosures of a GEC at both ends was expressly extended to include
- 5030At the service, the main bonding jumper connects
- 5031What is the minimum size copper main bonding jumper for a service with 4/0 AWG copper ungrounded conductors?
- 5032A service has four parallel sets of 500 kcmil copper per phase (2000 kcmil total). What is the minimum copper main bonding jumper?
- 5033A subpanel in the same building is fed by a feeder from the service. How must the grounded (neutral) conductor be treated at the subpanel?