A service has 500 kcmil copper ungrounded conductors. What is the minimum copper GEC to a water pipe electrode?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5020
- D: 1/0 AWG
Explanation
For copper service conductors over 350 kcmil through 600 kcmil, Table 250.66 requires at least a 1/0 copper GEC. A 500 kcmil service falls in that row.